  • Pizzarotic
    commented on 's reply
    Originally posted by dogshark58 View Post
    I am still at the planning stage though I have about 50% of my bricks cut before our Irish wet season started.

    I intend covering my hearth with polished granite as an impervious layer on which my underfloor insulation will sit. As the granite comes in 1m square tiles I’ll place weep holes to permit drainage.

    I would like some advice regarding insulation under the oven floor. From various pictures I see two options.
    1. The insulation it trimmed to match the shape and size of the oven ie circular.
    2. The insulation and oven floor are rectangular and much wider than the finished dimensions of the oven.
    Option 1 uses less insulation, my preference since insulation here is difficult to get and expensive. However, this involves more floor brick cutting to match the shape. I assume any oven or oven floor expansion compresses the insulation blanket around the inner oven wall.

    Option 2, If I use this method do I need to have something around the outer layer of floor bricks to keep the oven floor from moving. Would cementing the outer row of bricks to the granite keep it stable or would this inhibit floor expansion. Do I need to allow for floor expansion?

    Any suggestions as always welcome.
    Option 1 is the only option. The floor bricks can not extend out past the dome bricks or will be a point of significant heat loss.

    The floor bricks can either be cut to the inside of the dome bricks or the outside. Cutting to the inside of the dome can be more meticulous whereas to the outside you can be pretty rough as they get covered by the dome insulation.

  • fox
    commented on 's reply
    What size is your base and what size is your oven?

    Wont it be a bit wasteful and expensive laying polished granite under the dome?

    I always cut my ceramic board 5” bigger than the dome so the the bricks dont rest right on the edge of the board!

    Have you considered laying the granite at the same level as the oven landing, wont your suggested method see the granite around 7” lower than the oven floor surface?
    If you put the granite down first then 4” of insulation then 3” of brick .

  • dogshark58
    replied
    I am still at the planning stage though I have about 50% of my bricks cut before our Irish wet season started.

    I intend covering my hearth with polished granite as an impervious layer on which my underfloor insulation will sit. As the granite comes in 1m square tiles I’ll place weep holes to permit drainage.

    I would like some advice regarding insulation under the oven floor. From various pictures I see two options.
    1. The insulation it trimmed to match the shape and size of the oven ie circular.
    2. The insulation and oven floor are rectangular and much wider than the finished dimensions of the oven.
    Option 1 uses less insulation, my preference since insulation here is difficult to get and expensive. However, this involves more floor brick cutting to match the shape. I assume any oven or oven floor expansion compresses the insulation blanket around the inner oven wall.

    Option 2, If I use this method do I need to have something around the outer layer of floor bricks to keep the oven floor from moving. Would cementing the outer row of bricks to the granite keep it stable or would this inhibit floor expansion. Do I need to allow for floor expansion?

    Any suggestions as always welcome.

    Leave a comment:


  • mongota
    commented on 's reply
    Originally posted by dogshark58 View Post
    Mongo

    Also if I understand correctly the width of insulation around the dome enables the oven to expand and contract without cracking the external render.

    Could I ask what the red material is around the edges on your photo, is this a waterproof compound?
    1) Correct. My dome for example sits on top of 4" of board insulation. The completed brick dome was then covered with 4" of blanket insulation, and the blanket insulation was covered with expanded lathe and a hard render shell. I can fire my oven and because the 4 inch thickness of cushy blanket insulation isolates the brick dome from the hard render shell, the brick dome can move as needed and not stress the hard shell.

    2) The red stuff is RedGard. A liquid waterproofing membrane. I put it on my slab to prevent moisture in my slab from wicking up in to my board and blanket insulation. I had it on hand, so I used it. RedGard is NOT vapor permeable, so I would NOT use it over the render shell that covers the insulated dome. I DID waterproof my render shell but with Thoroseal. Thoroseal is a cement-based waterproofing that is waterproof (liquid waterproof) but it is also water vapor permeable. Water vapor can pass through it, but not liquid water.

    In an idle oven, one sitting over a wet winter for example, the oven structure may absorb moisture simply due to latent moisture in the atmosphere. When I fire my oven after a period of non-use, the fire will try to drive that moisture out of the oven. While the moisture can NOT pass through the RedGard (vapor impermeable) it CAN pass through the Thoroseal (vapor permeable) and then in to free air. I also have a vent at the apex of my dome. Moisture vapor driven out of the dome structure by the heat from a fire does exit the oven structure through that vent as well.

    Try to keep water out with proper detailing of your build. But plan on it getting in, thus provide an appropriate escape path. Just in case!

  • dogshark58
    replied
    Thanks Giovanni, will do

    Leave a comment:


  • Giovanni Rossi
    commented on 's reply
    dogshark58, Read through Mongo's build. The answer is there and the overall value is worth every minute it will take you to review. Giovanni

  • dogshark58
    replied
    Mongo

    Thanks for your prompt reply.

    I understand about no holes in the insulation, I expect this is because most moisture finds its way from outside the dome. Given the size of Ceramic board I will be using it will be two layers and I understand about staggering the seams,

    Regarding the footprint of the insulation / oven floor, I too am concerned about building the dome sitting right on the edge of the insulation. If I extend the insulation and oven brick floor I can square the edges of the floor more easily.

    Also if I understand correctly the width of insulation around the dome enables the oven to expand and contract without cracking the external render.

    Could I ask what the red material is around the edges on your photo, is this a waterproof compound?

    Leave a comment:


  • mongota
    commented on 's reply
    I may be reading this incorrectly, but you don't need drainage holes in your 4" thickness of under-floor board insulation. Your under-floor insulation should be continuous in my opinion. No drainage holes in the insulation itself, and with any insulation board seams offset from one layer to another if indeed you are doing multiple layers of board insulation to get the 4" total thickness. If one of the pro's has another idea on that, I'd be happy hear what they have to say.

    I'd venture that the drainage tiles should have the same footprint as your insulation footprint. While I did not use tiles under the insulation, my understanding is that the goal is to isolate any and all insulation from the slab to prevent slab moisture from wicking up in to the insulation. And to allow any moisture that does get in to the insulation a drainage gap between the insulation and the slab.

    With my dome, I extended the board insulation out past the footprint of the brick dome. I felt that was a good choice for two reasons:
    1) The dome bricks were not right on the edge of the 4" thickness of insulation. I felt that would minimize the possibility of the weight of the dome bricks compressing the 4" thickness of board insulation right at the edge of the board.
    2) When I insulated my dome, the first 1" thickness of blanket insulation landed on top of the floor board insulation. The following three layers of 1" blanket insulation covered the sides of the floor insulation, extending down to the slab. With the first layer landing on top and the following layers extending all the way to the slab, the seam between the blanket and board was not a linear path.

    I'll try to add a couple of photos. They help more than words.

    Best, Mongo





  • dogshark58
    replied
    I have spent the summer cutting my stock of fire brick and I am now turning my attention to placing my oven floor on the hearth.


    Having had previous useful comments and suggestions I have considered my next steps and have settled of the the following - all comments and suggestions welcome
    1. I intend placing a layer of glazed cheap ceramic tiles covering the footprint of my oven floor. These will have a drainage gap between them and weep holes through to the wood store below.
    2. I intend placing 100mm (approx 4”) of Ceramic fibre board on top of the ceramic tiles. The weep holes to match those below.
    My first question is in relation to the footprint of the ceramic tiles / insulation on which the oven floor will sit. Should this be...
    1. Trimmed to the size of the exterior walls of the dome?
    2. Extended to cover an area beyond the width of the exterior walls of the dome plus the width of dome insulation and final rendering
    What would the best practice be to enable the dome / floor to expand At this time I plan to go with option b leaving 2-3” of the extended oven floor beyond the finished rendering.

    I intend placing fire brick in herring bone pattern but placed on their edge which will give a fire brick height of 4.5” for the oven floor on top of the 100mm ceramic fibre board. Although using more fire brick my thinking is that this will provide further insulation and this build is in Ireland.

    Final question, I haven’t decided but I will either tile the remaining hearth or lay polished granite to butt against the protruding oven floor. I would see the granite being about 1-2” below the level of the oven floor. Do I need to leave a gap for floor expansion against the granite?

    Any comments of approval or suggested improvements are welcome.

    Leave a comment:


  • mongota
    commented on 's reply
    My "L" cut method was the same as JR described.

    The rope I used was 1/2" ceramic fiber rope, I used two pieces of rope, one stuck to the face and the other stuck to the side of the arch bricks. A thin bead of high temp silicon was my "glue".

    Because the rope was a bit thick (1/2") I also notched out a groove in the "L" of the bricks so the bricks could nest a bit closer together. I notched one brick, made a template, and used that to make my cut lines on the other bricks. Very easy to do with a diamond blade on the angle grinder.



    Enjoy your build!
    Best, Mongo



  • JRPizza
    commented on 's reply
    Some folks have cut L shaped bricks for the rear vent arch so that there is both an horizontal and vertical air gap between the dome arch and the vent. The horizontal gap makes a handy place to place a bit of insulation/rope without having to fight gravity to keep it in place. You can check out my build to see an example.
    https://community.fornobravo.com/for...326#post421326
    I've been working on my oven for a little while and have been debating starting a build thread, as I probably won't have much to add in terms of artistry or inventiveness over the excellent work already posted on this forum. That said, I thought I would share what I have done and hopefully continue to get
    Last edited by JRPizza; 09-09-2021, 07:26 AM.

  • dogshark58
    replied
    I am currently busy cutting bricks and up to the 7th course of by 42” build. Having exhausted my initial purchase of fire brick, I’m calculating what I need to complete including the external arch, entrance and chimney.

    I have seen some discussion on leaving an expansion gap between the entrance / external arch and the main oven.
    1. should this simply be a gap with the external insulation fibre and vcrete hiding it?
    2. Are there other methods to install insulation between the dome and entrance to leave an expansion gap
    As always any wisdom is appreciated.

    Leave a comment:


  • wolfmoonex
    replied
    A popular insulation stack is Cal sil > inverted bathroom tiles to drain moisture > foam glass > perlcreate

    Leave a comment:


  • david s
    commented on 's reply
    I use an additive in the concrete mix which makes it waterproof when I cast the supporting slab. Another alternative is to coat the top of the slab with a sealer. These treatments should prevent or at least reduce moisture wicking up from the stand, but will not prevent refractory material from absorbing moisture from the air in periods of very high humidity. In that case neither will a roof. We live in the tropics and during the wet season I’ve experienced times when the oven has picked up moisture from very high humidity even though it hasn’t actually rained. Knowing how wet Ireland is, you may have similar problems with high humidity. A long gentle fire or two does the trick of restoring normal function.

    Also make sure no sprinklers wet the stand on a regular basis, this has proved to be a problem with water wicking up the stand.
    Last edited by david s; 05-24-2021, 12:19 PM.

  • SableSprings
    commented on 's reply
    Dogshark58, my only concern is if the quarry tiles will wick water as does concrete. The reason I like to see ceramic/mosaic tiles used is that they are impervious to water transfer. If you put a quarry tile in a bucket of water for an hour...does it absorb water (gain weight)? If it does, then it would not be suitable to create the waterproofing layer on top of the concrete hearth.