  • Any thoughts on electrically ground a tall stove-pipe (and support pole)?

    I'm trying to learn how lightening grounding usually works. It seems like a conventional approach is to use a nearly 4' solid copper rod driven all the way into the ground...that's expensive.

    Any ideas? Is copper necessary? Is 4' necessary?

    Website: http://keithwiley.com
    WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
    Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

  • #2
    Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

    It's about conductivity conductivity of metals. You could substitute copper with silver, but some how I don't think you'd like that any better.

    Thick 1 cm (2/5") bare copper wire will also do the grounding trick if it's long enough. It's dug at least 0,5 meters (2 feet) to the ground (usually in a circle around the protected building).

    Something like this
    Last edited by Laku; 07-15-2012, 01:08 AM.

    Comment


    • #3
      Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

      I realize copper is more conductive than other typical materials. What I don't understand is why it makes any difference in a lightning rod. The current is going to follow the available path of least resistance and just about any metal would make a good path for electricity to follow...so wouldn't a steel spike direct lightening into the ground just as easily?

      By the same logic, if only copper will do, so how does attaching a cable to the foot of my aluminum pole work at all? Don't I need to lead a copper cable up to the top of the pole (and a second cable up to the top of the stove-pipe)? Neither of those is made of copper. One is stainless steel and the other is aluminum. What do those not have to be copper by the spike in the ground does? I'm sorry, I just don't understand that.

      Website: http://keithwiley.com
      WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
      Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

      Comment


      • #4
        Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

        Other metals do conduct better than most of other stuff, but the more conductive it is the more sure the lightning will travel along that path and not jump/fork to something you don't want it to. Then there's also corrosion to consider. Also the less conductive then more resistive the material is and that will cause it to heat more when passing current trough --> additional fire hazard.

        That's how I've understood it, just a layman's opinion though so keep that in mind.

        Comment


        • #5
          Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

          Right, but is the implication that I should not only use a copper spike in the ground, but also that I should run heavy gauge copper cable up to the top of my support pole and also to the top of the stove-pipe?

          That seems absurd, but it's one or the other. I mean, I don't see much purpose in using copper at and below ground level to ground a tall metal structure which isn't copper. Am I wrong? Is it perfectly sensible to use a copper spike to ground an aluminum pole and a steel stove-pipe?...or should I just go ahead and just steel (the more conductive of the two metals involved in this discussion).

          Website: http://keithwiley.com
          WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
          Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

          Comment


          • #6
            Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

            I think it is, considering the huge amount of current lightning will produce.

            I think they only connect the corners on metal roofs to grounding, so don't know about having to run the wire all they way top. Then again the amount of metal in a roof will ensure that the resistance isn't going to get high enough to set anything in fire.. I think

            Way I see it the copper is best suited material to transfer enough current and still be discreet as possible. Other metals would need to be thicker to pass through the same amount of current without heating too much.

            here's something on the subject I found with quick search

            Comment


            • #7
              Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

              On the electrical poles down here they have the copper attached to the full length of the pole. The wire is twisted into a coil and attached underneath the base of the pole. When the pole is set, the weight of the pole is setting on the coil of copper. I think the coil of wire must give it more area of contact with the earth. Of course they do require grounding rods at the service entrance of the home, though. The reason copper is requred for earth contact is that steel will eventually turn into a ball of rust and probably would be less of a ground at that point. I think that your aluminum pole would have enough mass to be a good conductor. I would just run a copper ground from the top of the chimney to the pole. Then I would secure another length of copper wire to the base of the aluminum pole and then to a copper ground rod.
              Joe Watson " A year from now, you will wish that you had started today" My Build Album / My Build

              Comment


              • #8
                Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                Thanks Gulf. Sounds expensive. I actually suspect the 4" to 3-1/2" aluminum support pole doesn't provide more metal for electricity to flow through than the 7" double-walled steel pipe, despite the pole's 1/8" thickness (since the stove pipe is two concentric walls of significantly greater circumference than the pole, and I believe steel is more conductive than aluminum, so for a given thickness it generates less resistance...I think).

                Of course, there's the question of whether the support arm between the two structures is solid enough to transmit lightening from one to the other such that I need only ground one of the two structures (ostensibly the pole). I have been considering using copper pipe as the support arms between the pole and the stove pipe, just for aesthetic reasons. Perhaps this is another good reason for that approach. :-)

                I'll see what copper cable costs, I don't want to spend as much on a lightening system as the rest of the system put together. Good grief.

                Thanks.

                Website: http://keithwiley.com
                WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
                Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

                Comment


                • #9
                  Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                  I seriously doubt that this thing will ever take a strike. There are several 80-footish trees in the immediate viscinity (within thirty-forty feet of the oven) and a church steeple just two lots away (to say nothing of my own house's roof, which will be of comparable height and only thirty-forty feet away).

                  Part of the reason for this super long stove pipe is that the oven is on really low ground. In the end, after I build this thing, the top of the stove-pipe will still be lower than that of many other roof-stove-pipes in the area. The only thing that makes it look so electrical is that it will be one rather long pipe instead of a short pipe one top of a roof (and the 14' support pole next to it).

                  Cheers!

                  Website: http://keithwiley.com
                  WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
                  Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

                  Comment


                  • #10
                    Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                    There's a formula of a sort to that kind of protection



                    How trees (and tall buildings/structures if conductive enough) affect protection angle

                    Trees all around the building alpha= 60?
                    Trees on two opposite sides of the house alpha = 50?
                    Trees on one side of the house alpha = 30?
                    Solitary tree alpha = 25?

                    Everything that is inside of that is almost perfectly protected.

                    Comment


                    • #11
                      Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                      Yeah, see, by that analysis alone, I barely need any grounding. I'll ground it for sure, I'm just not sure I'll obsess over it or spend $150-$200 on gobs of copper.

                      I'll look into it carefully as I proceed.

                      Website: http://keithwiley.com
                      WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
                      Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

                      Comment


                      • #12
                        Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                        ".......Sounds expensive. I actually suspect the 4" to 3-1/2" aluminum support pole doesn't provide more metal for electricity to flow through than the 7" double-walled steel pipe"

                        About 30 bucks for an 8' grounding rod. $2.50-3.00 for the clamp and about $1.25 per foot of bare copper wire. I do agree that the steel in your chimney would probably be a better conductor than the aluminum pole. That is why I would ground them together at the top and only ground the aluminum pole to earth. Hopefully, a charge would follow the better grounded aluminum and away from the oven.
                        Joe Watson " A year from now, you will wish that you had started today" My Build Album / My Build

                        Comment


                        • #13
                          Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                          Originally posted by Gulf View Post
                          ".......Sounds expensive. I actually suspect the 4" to 3-1/2" aluminum support pole doesn't provide more metal for electricity to flow through than the 7" double-walled steel pipe"

                          About 30 bucks for an 8' grounding rod. $2.50-3.00 for the clamp and about $1.25 per foot of bare copper wire. I do agree that the steel in your chimney would probably be a better conductor than the aluminum pole. That is why I would ground them together at the top and only ground the aluminum pole to earth. Hopefully, a charge would follow the better grounded aluminum and away from the oven.
                          I was perusing ebay and hadn't found 8' rods yet. Found lots of 4' and a few 6'. If I used the 4' I would probably buy two or three (not sure if the proper wiring is serial or parallel w.r.t. the base of the pole.). My yard is riddled with rocks the size of a cantelope, I can't even drive 12" tent stakes without stopping to dig out the hole as I go. Going down 4' for the shorter rods is going to be almost impossible; it's going to take me a full day to dig that far down (times 2 or 3 for multiple rods). Going down 8' will definitely be COMPLETELY impossible in my yard (without renting a backhoe and destroying the yard in the process).

                          Website: http://keithwiley.com
                          WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
                          Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html

                          Comment


                          • #14
                            Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                            Sorry Kebwi,
                            No experience with rocky soil and 8' is all I have ever delt with. They probably use a rotary hammer in that kind of terrain. If you haven't poured the base for your pole yet, you could coil a good bit of bare copper wire at the bottom of it and run it up the side of the pour. I would cover it a little to keep most of it seperated from the concrete.

                            I'm not even sure that I would go to the trouble, just throwing out ideas.
                            Joe Watson " A year from now, you will wish that you had started today" My Build Album / My Build

                            Comment


                            • #15
                              Re: Any thoughts on electrically ground a tall stove-pipe (and support pole)?

                              Yep, it would seem to be a natural fit to exploit the post hole as a start for the rod. Unfortunately, my post hole will be almost perfectly insulated. It isn't actually a hole so much as the gap between a brick retaining wall (obviously pretty nonconductive) and the back of the oven stand (concrete blocks) and the concrete slab on which the entire oven sits extends within an inch or two of the retaining wall so the hole will have a concrete floor under it. I'll put some gravel at the bottom before I pour the concrete so it will drain any rain water into the crevice between the concrete slab and the retaining wall, but there's no way to dig down there, so the rod can't go there.

                              Nope, the hole for the copper rod starts at ground level (up on top of the retaining wall I expect).

                              Oh well. :-)

                              Cheers!

                              Website: http://keithwiley.com
                              WFO Webpage: http://keithwiley.com/brickPizzaOven.shtml
                              Thread: http://www.fornobravo.com/forum/f21/...ttle-7878.html