    Our goal is not to harp on the issue but to make you oven the best it can be. With all your hard work of planning and design, it will be a great oven. A 5 to 1 pecrete mix is suggested for under the floor and dome since this ratio has enough compression strength for supporting the dome and floor and adequate insulation value. Roughly 4" 5 to 1 pcrete equals 2" CaSi. So a total of 4" CaSi equivalent is a very good insulated floor.
    Click image for larger version

Name:	Vcrete K values.jpg
Views:	442
Size:	159.3 KB
ID:	471445
    Russell
    https://photos.google.com/album/AF1Q...L9lr_UnUgJbF3Z

    Comment


    • #47
      I have almost everything I need to build the oven purchased and stored in dry basement over winter, I already purchased perlite, "Ceramic fibre blanket 2300°F 1'' 8LB/FT3 (1 Box 47.3sf)", and 5 count of "Ceramic fibre board 2300°F 2'' X 12'' X 36''" . I even have ThermoBond 915 100lbs refractory mortar purchased about a year ago placed in tight closed plastic pail never opened yet. The only thing I haven't got yet is either refractory castable or a steel plate for the doughnut base. so my design requires using ceramic fibre board under insulation not CaSi board

      for weeping holes, I could even cut using my concrete saw shallow channels grid all over the slab; however unfortunately, at this moment, I am still not sure I need to do anything for making a "pooling water" drain from a hole because: I have a 6" thick slab placed mostly on grouted cmu block cores with very little gaps under it and still connected to a bottom slab that is 5.5" thick ... and got lots of fibre on slab. I can't imagine the oven can produce enough moisture to saturate close to 3 tons of concrete between firings . I most likely be a light user of the oven, may be fire it few times a year or so (not good to plan to design it so though). I have a feeling that weeping holes would be more suitable for large open span slabs with wood being stored under the oven that the slab would be bowed in centre creating a gap between the oven base and the slab where it will get filled with no emptiness but moist air. My priority in my oven is to have extremely rigid and stable foundation that will not propagate settlement to oven and water should not get on it. I still have close to a month to research it more and decide , for now just waiting for concrete to cure.

      any help about my insulation stack design and if I should use castable refractory for dome wall support or instead use a 1/4" mild steel sheet one? as I am not using tiles under the dome walls, the ceramic fibre board and perlite if they creep or settle could cause settlement on a half brick and that if combined could cause a dome instability, so wanting to put a very solid doughnut under the dome walls ONLY while hearth can be on its own ...
      ​
      Last edited by IH123; 06-07-2026, 06:47 PM.

      Comment


      • #48
        Originally posted by IH123 View Post
        I have almost everything I need to build the oven purchased and stored in dry basement over winter, I already purchased perlite, "Ceramic fibre blanket 2300°F 1'' 8LB/FT3 (1 Box 47.3sf)", and 5 count of "Ceramic fibre board 2300°F 2'' X 12'' X 36''" . I even have ThermoBond 915 100lbs refractory mortar purchased about a year ago placed in tight closed plastic pail never opened yet. The only thing I haven't got yet is either refractory castable or a steel plate for the doughnut base. so my design requires using ceramic fibre board under insulation not CaSi board

        for weeping holes, I could even cut using my concrete saw shallow channels grid all over the slab; however unfortunately, at this moment, I am still not sure I need to do anything for making a "pooling water" drain from a hole because: I have a 6" thick slab placed mostly on grouted cmu block cores with very little gaps under it and still connected to a bottom slab that is 5.5" thick ... and got lots of fibre on slab. I can't imagine the oven can produce enough moisture to saturate close to 3 tons of concrete between firings . I most likely be a light user of the oven, may be fire it few times a year or so (not good to plan to design it so though). I have a feeling that weeping holes would be more suitable for large open span slabs with wood being stored under the oven that the slab would be bowed in centre creating a gap between the oven base and the slab where it will get filled with no emptiness but moist air. My priority in my oven is to have extremely rigid and stable foundation that will not propagate settlement to oven and water should not get on it. I still have close to a month to research it more and decide , for now just waiting for concrete to cure.

        any help about my insulation stack design and if I should use castable refractory for dome wall support or instead use a 1/4" mild steel sheet one? as I am not using tiles under the dome walls, the ceramic fibre board and perlite if they creep or settle could cause settlement on a half brick and that if combined could cause a dome instability, so wanting to put a very solid doughnut under the dome walls ONLY while hearth can be on its own ...
        ​
        The problem is that water is conductive, air is not. This leads to moist insulation not working as an insulator. This fact combined with water in a liquid state creating more than 1500 times its volume as steam when heated, means that small amounts of water will negate the insulative quality of the insulation. Every oven owner becomes surprised by just how much is generated and how much difference it makes to the efficient operation of their ovens.

        Any mild steel used in the build particularly if thin, is prone to corrosion from the combination of heat and moisture, always use stainless.
        Last edited by david s; 06-09-2026, 12:38 PM.
        Kindled with zeal and fired with passion.

        Comment


        • #49
          it all depends on the form of water and where the oven is. In Calgary, water is:

          -water=ice
          -water=nightmare in -40C, -20C, 0c
          -water can turn ice from October to May
          -steam water will turn to ice powder in cold weather
          - water= damage as it expands and freezes


          having weeping holes on slab in winter is not very useful because they will certainly get blocked and ice, only way to get them open is if concrete temperature rise above zero for a while which probably will not happen for hours of firing because of insulation and outdoor temperatures and wind .

          A positive thing of living thousands of kilometres away from warm ocean with sun taken vacation for whole winter is outside air is mostly dry so water can fly free when not too cold


          Therefore, protecting oven from downpour is the best thing someone like me can do, moisture build up inside oven will be limited to water content inside oven cooking chamber from food and fuel. The thinking of water coming from air vapour and becoming water pooled inside insulation will not apply much as I think dealing with designing an exist for water from a confined place will be unworthy knowing the oven got a mouth and a chimney to vent off. might be best way to adapt is to slow fire each time and master how to get the oven to dry as it warms up
          Last edited by IH123; 06-10-2026, 03:37 PM.

          Comment


          • #50
            Water expansion on freezing is around 9% and in Calgary is certainly something you need to be wary of , but when it turns to steam can expand more than 1500 times which is 150000% and something oven builders need to consider wherever they are. Water will eventually be eliminated by fire, but its exit is far quicker and simpler if an exit path is provided, just like a fire exit in a crowded hall.
            The way you have built your stand will not allow for drilling holes from underneath once the oven is built over it, so plan carefully.
            Last edited by david s; 06-11-2026, 12:32 PM.
            Kindled with zeal and fired with passion.

            Comment


            • #51
              Originally posted by david s View Post
              Water expansion on freezing is around 9% and in Calgary is certainly something you need to be wary of , but when it turns to steam can expand more than 1500 times which is 150000% and something oven builders need to consider wherever they are. Water will eventually be eliminated by fire, but its exit is far quicker and simpler if an exit path is provided, just like a fire exit in a crowded hall.
              The way you have built your stand will not allow for drilling holes from underneath once the oven is built over it, so plan carefully.
              ​ Click image for larger version

Name:	Untitled.jpg
Views:	298
Size:	125.2 KB
ID:	471531

              if I lay rebars on top of concrete slab then pour the perlite-cement on them (as shown in above image), after the layer is cured, the rebars can be pulled out leaving a hollow channel in the insulation layer where water can seep out, the channels will meet near the oven mouth area, then concrete saw shallow cut on concrete slab will channel the water further to the front edge of the concrete slab (there is no insulation there, finally a 1/2" hole is drilled at about 10" away from the front edge of the slab allowing any water to weep and drain there. of course, the water channel can be covered with a masonry layer/sheet later to prevent water from back flowing. It might be that half of those channels are needed (like 5 or 3 instead of 9. what do you think? does that work?

              Comment


              • #52
                This idea should work quite well. Because rebar contains ridges designed to increase grip and reduce pull out I think some plastic conduit wrapped neatly in plastic would be far easier to pull out, but I’m sure you’d work it out. Also spraying with cooking oil helps release anything from concrete work.
                Kindled with zeal and fired with passion.

                Comment


                • #53
                  That is something new, will be interested on how this works. Remember, even 5 to1 pcrete seems crumbly until it sets up so don't pull out too soon. Dave brings up a good point on the rebar ridges but maybe the vapor barrier will solve the friction issue of pulling the bars out. What about reversing the direction of the weep hole and rebar then the weep hole is in the back of the oven slab, out of sight out of mind.
                  Last edited by UtahBeehiver; 06-12-2026, 05:11 AM.
                  Russell
                  https://photos.google.com/album/AF1Q...L9lr_UnUgJbF3Z

                  Comment


                  • #54
                    Originally posted by UtahBeehiver View Post
                    That is something new, will be interested on how this works. Remember, even 5 to1 pcrete seems crumbly until it sets up so don't pull out too soon. Dave brings up a good point on the rebar ridges but maybe the vapor barrier will solve the friction issue of pulling the bars out. What about reversing the direction of the weep hole and rebar then the weep hole is in the back of the oven slab, out of sight out of mind.
                    reason to use front:

                    1) I plan to put my feet in the 12" between slab front edge and the front wall, that will make my feet under the slab while my body flush with the slab edge and then my arms can extend toward oven mouth with more reach of the 12"
                    2) oven mouth will be 12" away from slab front edge that if I stand at slab edge I will be far. reason of leaving the 1ft on front is to allow to rest the pizza on.
                    3) I plan to store wood in the 12" space at the back under the slab, less space is possible in front where my feet will go. should use external wood storage like a shed for long term (may be not to avoid mice).
                    4) the top concrete slab is naturally 1-2 degree sloped forward (front lower than back)so its easier to have the dripping water drips forward than backward avoiding additional back sloping

                    Comment


                    • #55
                      how about that:
                      1)a hole cut straight through the top slab into the open air space beneath CMU block walls will turn into a cold-air intake. When oven is hot, it will draw cold, damp air up through those drainage holes right into the insulation.

                      2) Freeze-Thaw Ground Moisture: In the spring, melting snow and ground moisture under oven base will evaporate upward. Those open holes in the slab will act like funnels, sucking ground humidity directly into perlite and ceramic fiber layers, causing the exact water-logging issue I am are trying to prevent.​


                      3) heat-loss paths,
                      4) moisture migration paths
                      5) insect nesting locations (even using stainless steel mesh, if its not to fine mosquitoes can get in or smaller flies, even crawling insets trying to hide from cold winter. too fine one may clog the channel/hole as debris and dust fills it)
                      6) collection points for debris.​

                      ??

                      Comment


                      • #56
                        No, air movement by convection requires it to be open at both ends. If really concerned about this point they could be plugged when not required. There’s far more heat loss from the oven mouth because of its much larger area. In high humidity even a roof won’t hold out moisture. We live in the tropics, oven is out in the weather, but I did have an occasion when after drying and using the oven, two weeks later in a period of very high humidity, but no actual rain, on heating the oven again, the outside shell was hot after an hour of firing, which indicates the presence of moisture in the insulation layers.
                        Any weep holes should be covered with insect mesh.
                        Kindled with zeal and fired with passion.

                        Comment


                        • #57
                          would it be equivalent or better to remove the perclite layer from bottom insulation completely and instead add one more 1" of ceramic fibre board to have total 3"? should I or have to make it 4" for hearth?

                          Comment


                          • #58
                            Dry board removes the need to dry a vermicrete slab after it’s laid and cured,but is a more expensive alternative. Regarding insulation thickness some say you can never have too much, but it does conform to the law of diminishing returns so efficiency needs to be balanced against cost. If you go with dry insulating board, raising the board away from the supporting slab with tiles and their adjoining gaps, is probably the best solution.
                            Last edited by david s; 06-16-2026, 11:04 PM.
                            Kindled with zeal and fired with passion.

                            Comment


                            • #59
                              If you can find it, FoamGlas is an alternative to P/vCrete or CaSi for the first layer. It will not absorb or transmit water and has similar K value to CaSi. I used it in my build but it is difficult to find.

                              Click image for larger version  Name:	30A Brick Floor on Insulation edited 2.2014.jpg Views:	5 Size:	153.8 KB ID:	471627
                              Last edited by UtahBeehiver; 06-18-2026, 03:52 PM. Reason: Wrong name
                              Russell
                              https://photos.google.com/album/AF1Q...L9lr_UnUgJbF3Z

                              Comment


                              • #60
                                ok, so while I already have 5 ceramic fibre boards 18lbs/cu ft each 12"x36"x2", I have bought to be delivered July 10th 8 Skamol calcium silicate boards each 58cm x 24cm x 4cm. I want to design my oven for certain conditions with 1000F inside and at ambient temp outside of lets say 100F, would those two layers of casi+cfb equivalent to about 3.5" thick be enough on that hot day and hot oven firing that concrete slab under them wont reach more than 125F? otherwise if I add a 2.5" 5:1 perlite cement under then do I need to worry about Calgary winter freeze(--37c in extremes I seen that average -25c easily ) that it would destroy the moisture soaked perelite-cement layer causing unstable base?

                                casi+cfb at 3.5"thick, what else do I add if any:

                                1) nothing, concrete slab gonna be very fine under them
                                2) 5:1 perlite cement layer 2.5" thick, how to deal with winter freeze as the temp wont reach boiling point on it to evaporate water in it
                                3) loose perlite in a container made of pavement concrete bricks mortared to base slab and tampered or crushed a bit, lets say about 3" thick
                                4) another 1" or 2" casi?
                                5) another 2" ceramic fibre board?

                                I am using 2 bags of Quikrete Sand/Topping Mix 25KG Model # 110326​ to level the slab as well as green self levelling laser level on tripod. I guess most likely no need for the 2.5" perlite-cement layer
                                Last edited by IH123; 06-24-2026, 09:40 PM.